Technically the id and id plus systems are interoperable. However in practice this is not always the case. The voltages used by the 2 biscuit variants is slightly different. Many companies that used to use iD have a large stockpile of the old biscuit type to support legacy systems due to this issue.
iD whilst owned by honeywell, they dont actually make a control panel to support them.
Texecom, Castle care tech and menvier currently do, however its a dying tech, texecom recently announced they would be pulling support for iD
If it was operational before then you have either damaged something on the connections or board or not seated the control panel tamper switch correctly.
There are 2 issues here. Systems such as this are not normally used for recognition capture. If you want to capture regs then lens size or scene width are the most important aspect. You want to be viewing approx a scene width of approx 6m at the point of reg capture. You also need to be facing the reg in question with the camera. Too much offset angle will make it harder.
Usually the old obs kits just sent video over the cores not a twisted pair converted signal.
Its not supported but you should be able to open a cable and test for power and video. However bear in mind some kits were actually line fed. I would suggest it be a better idea to replace the cameras with some not locked to that monitor
Any NC door contact would be suitable ie
ie http://www.securitywarehouse.co.uk/catalog/index.php?main_page=product_info&cPath=36_44&products_id=667
but it may depend on your door. What are your protecting?
You need to narrow down which tamper is the issue.
ID loop out the global tamper, keypad tamer (if a gen4) and SAB tamper.
If you can upload a photo of your board i can see which tampers are in use.
Im afraid we dont support zoneminder. I do watch the project however.
I have not tested the cards we have with zm as for my own use I only use IP cameras.
James
If you dont wire it this way or use a dedicated line. Anyone picking up the phone will prevent the system dialling out.
Sales will update the other point
Adding or replacing user fobs is a manager function. Is the local led on the unit working, ie is the battery installed correctly.
WHat process are you using to add the fob?
If you click on the above picture you will see a set of terminals for 'line' and 'set'
The line connection pair is the tel line connector. You can plug it in but this isnt the best connection method.
If you connect the line connections to 2 and 5 respectivly in your master socket plate
Are you looking at a particular unit?
Most accept upto 4 telephone numbers but are generally regarded as a low security device (just like any voice / text dialler)
That is a basic logging function. Any of the higher end panels will do this. IF you dont currently have the software id look at the texecom premier range. Their software is called wintex and can be used to connect via a compatible modem. You can the download your events and print etc
The smaller panel can only handle 1 partition, but i wonder if your mixing up part set and partition. If you need more than 1 partition you need the more powerful panel.
A partition in this case is to create a separate logical system that is full set etc independently. Normally only used on commercial systems
Yes there is a reader in the panel
It can do voice dialling but will require gsm and an active sim etc for texting