Id advise a siemens eline dt in that situation. Its the best pet sensor I've personally tested. But the only 200% way is to use perimeter protection, ie vibs and contacts
Could be but id be surprised. First I check day mode current Dc supply voltage at the detectors And ac ripple on the cabling What do you have connected to the panel? If you could post the readings above please
As you have rasied a ticket it will be discussed here to.
But as i dont have that info just yet was it all ordered together or are you adding older kit to new gear?
Vibs will be fine but you need to factor in the reduced real detection area on plastic. As with all perimiter protection has the same same fa causes. If fitted incorrectly. Most common on plastic doors and windows is to have too few units covering a too large an area
1 yes you are correct you only need links on unused inputs
2 the alarm will sound when you power it up ie when the mains is connected
3 yes that is for the optima
yeah thats fine. But on small runs with low device count you wont need the 680 ohm end of line resistor. Id wire as you have drawn but leave link 1 in and dont fit the eol resistors.
To be fair thats an excellent fault diagnosis report.
But the rf rx led's do indicate recieving something not always from the tx. If its not paired then its just normal noise.
Is it funtioning? is the question why the leds, or is it not functioning?