  1. Id agree with you. Might want to look at the M12 unit as that is programmable for fixed heat/rate of rise heat/smoke and/or any combination so covers most installs. Glad your sorted. James
  2. when you say you have wired to zone 3 do you mean you have connected A & B to zone 3? you will need to program the zone. The only things i can suggest is test the relay on the detector with a meter. Also your panel isnt in EOL configuration is it? How are you testing it? and where are you expecting the sound to come from, ie of the panel is programmed for double pole and correctly set up, disconnecting A or B should result in an alarm at the panel.
  3. good! yes the panel comes with user and engineer manuals
  4. Derry Yes the accenta can be programmed for 0-99 minutes of bell delay. However id urge caution on its use on a non police response system
  5. no the fish tanks should be fine. As long as there is no air movement from them. Also a PIR will not detect through glass. example detector http://www.securitywarehouse.co.uk/catalog/index.php?main_page=product_info&products_id=1007
  6. lol Anytime James
  7. Its not zoneminder for windows but a frontend for a zoneminder unit. http://www.zoneminder.com/wiki/index.php/ZM4MS
  8. Jiroma Its page 38 in the engineering manual Its in the part set menus
  9. Lingo Yes it is something that we do. You need to raise a support ticket asking for a vat free account. Please include your vat number and compnay details etc on the ticket. Once that has been approved your account will be set to vat free. James Support
  10. Done. Renamed *.zzz sent to both address's I will edit your email address in the above post to prevent abuse. James
  11. Lorand I did email it. However gmail sent me this back If you have an alternative address you can let us have, or i can send you a link for direct download over pm. James
  12. Lorand I have emailed you a version zipped using a lower compression. Let me know how you get on. James
  13. If i recall. (i dont have access to my manuals) then B1 and B2 are output 1 and 2. These are then programmed as bell and strobe by default.
  14. anytime Stuart James
  15. ok so using your supplied current draws 7 x 16mA = 112mA 4 x 7.5mA = 30mA 112mA + 30mA = 142mA 142mA = 0.142A so unless you have a maglock on it somewhere i reakon youve got your decimal points mixed up James
  16. Id suggest you are getting your decimal places mixed up. What have you calculated your total load to be?
  17. Tynesider. It does sound like you have a faulty simpleset. Id advise you raise an RMA request and get it swapped. James
  18. OK. you sure it doesnt have a 10A range if you move the leads?
  19. Yes i would have a single keypad on it as well. My bad i assumed you had an optima. I should never assume! Have you got more then 1 simple set reader? If so is that functioning as expected?
  20. Easiest way to get a day mode current is to put your meter in series with the battery and remove the mains. All current will then be off the battery and will give a quescient current. Once that is done put the mains back on and meter the batt leads with the batt disconnected and connected. That will give us a charge voltage. James
  21. The standalone reader will only give you a volateg output on valid tag/card. The HID unit will output data. However this infomation is not in the public domain. Depending on what you want to do, you would be better off going for an access system based on ms sql and then queriing the db direct, or using a system that gives a 232 output and getting your data from their. Actually reading the data reader would be difficult IMO. James
  22. as118150 Whats the day mode current of this panel? ALso the charging voltage would be useful. As a side note, what detectors on on this panel? ANd what battery is in it / age?
  23. Tynesider. Sorry I missed your thread yesterday. Nice detailed post AM i right in thinking from the post you have a problem with a simple set reader? If so, i would remove it from where it is fitted, disconnect all keypad wiring at the panel and just wire the one simple set in. If it works then we have eliminated a hardware fault. IF not it looks like we have a faulty simplset. 25m is fine. James
×
×