[Ticket Question] Rafiki twin flex 8 zone panel


Recommended Posts

Hi,

5 Zones enabled but only zone 5 is sounding when sounders set off, the other 4 zones are not responding when you set call points off or test the detectors. i also have a earth fault that wont go away i have earth continuity on all zones and at the panel. Its the first time i have installed a 8 zone panel are they much different from the 2 and 4 zone ones. 

Thanks

Link to comment
Share on other sites

An earth fault is usually due to a cable fault or a core shorting to earth somewhere. You will need to find and recitify this before anything else.

8 zone panels are the same just bigger. Ensure you havnt connected the cable shield (it isnt a functional earth) to any devices or back boxes.

Link to comment
Share on other sites

also check the earth cable that comes from the mains. There should also be a green/yellow earth cable that connects to a terminal on the PCB and if it isnt connected, it can show an earth fault.

 

In regards to the zones not working, are you getting any zone faults? If so does the LED flash faster than the buzzer or at the same rate as it?

 

Are you sure you switched the zones ON in the engineers menu???

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use.