securitywarehouse Posted September 9, 2010 Share Posted September 9, 2010 Hi, I need support with my powermax plus control panel, I have had my system working fine for around 11 months. I am having trouble disarming the system with the panels keypad, i get to 3 digits and then it just beeps. I have changed the code and it is still happening. All the buttons seem to work fine and i can disarm ok with the keyfob. Can you provide a solution or where i need to go for help? Or do i need a replacement panel?Many Thanks Quote Link to comment Share on other sites More sharing options...
accounts3 Posted September 13, 2010 Share Posted September 13, 2010 Hi I have not heard of this happening before, so we have contacted Visionic and will reply when we have spoken to their technical dept. Bear with us Anne Quote Link to comment Share on other sites More sharing options...
accounts3 Posted September 13, 2010 Share Posted September 13, 2010 Visonic are going to investigate this, as they say your keypad must be working for you to be able to change the code. Quote Link to comment Share on other sites More sharing options...
accounts3 Posted September 13, 2010 Share Posted September 13, 2010 Hi This is part of the set up. For EN & DD243 system the standard allows for fob only setting, the keypad can only be set to be used on non police calling systems. This is in the programming in panel defintions. off by wirekless/off by keypad. Best of luck Quote Link to comment Share on other sites More sharing options...
Secware_Tech6 Posted September 23, 2010 Share Posted September 23, 2010 agreed. By dd243 6.4.5 you cannot use a user code to disarm during entry. you can however disable this feature if dd243 isnt relevant Quote Link to comment Share on other sites More sharing options...
Recommended Posts
Join the conversation
You can post now and register later. If you have an account, sign in now to post with your account.