May 10, 201015 yr I purchased 2 M12 smoke detectors from you, which I wish to use with the Honeywell Accenta Mini Gen4 security system. The engineers manual shows 2 wires, to a smoke detector with a relay base for output to intruder system. On the M12 do I use the 0v +12v terminals or the fire zone?
May 10, 201015 yr No On the M12 you will have N/c and C connections. These connect to your zone wiring on the panel. THe 12v + and - connect to the panel + and - connections.