Recommended Posts


got around to installing the pyronix twin alert and the bell output is nice and loud but the spk just clicks? I have it set on a entry/exit output on a galaxy G3 panel and have moved the volume control. To debug I moved the wire I have going to the bell side to the spk and it don't sound? I even tried using the pull up resistor, still didn't work... I know I was somewhat brain frazeled by the time I got to do that (I even wired a sensor to the wrong zone lol) and wondering if I have missed something.. +12v -0v Spk switched to 0v Bell switched to 0v
Link to comment
Share on other sites

the spk input is just that. its not a switched input connection. You need to use the spk connection on the panel. However on that panel i would use a dedicated 16 Ohm speaker rather than a combined. If using a combined use something with a low and a high input and use outputs instead of speaker

Link to comment
Share on other sites