June 8, 201510 yr I am looking at purchasing the Honeywell Galaxy Flex 20 UK Panel together with ESP Fireline smoke and heat detectors. Can these be used in conjunction with one another i.e. integrate the detector system into the alarm panel, setting it up as a fire zone? Or are the ESP Fireline detectors only suitable for a fire panel?
June 10, 201510 yr No you cant you will need a 12v detector. Honeywell do a 12v non latching base for their detectors