I recently purchased from you a Siemens SPC530.320 alarm panel and Invincibell Plus amongst other compnents

 

My question relates to connecting wiring the Invincibell to the SPC530 panel.

In the Invincibell wiring diagram it shows the Bell terminal of the alarm box connected to the bell terminal of teh alarm panel. However on a Siemens SPC530 there is no terminal marked bell so I would like to confirm where the bell terminal of the invincibell should connect to on the Siemens SPC530

 

SPC

----------------------------------------------

----------------------------------------------

 

Com-------

NO---------

BHO------

TR------

EX------

EX+------

 

I also plan to have two Invincibell's connected in the citcuit (front/rear)

An example if you have one would be very much apprecaited

 

Regards

 

Gary

Link to comment
Share on other sites

you will use one of the programmable outputs programmed as bell for your bell connection. There should be a wiring diagram in the manual for your bells. But personally id of gone for a cqr bell as they are easy to wire up in 2 way.

Link to comment
Share on other sites

  • 1 month later...

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use.