Jump to content
Security Warehouse Support Forum

Scantronic 9651: Mains Fail - Log Report


Nhoj

Recommended Posts

Having just commissioned a 9651 I've been testing out event logging for the system.

I isolated the mains supply, hopping to invoke a mains fail alert. The RKP recorded the event properly, but interrogation of the event log showed no mains fail alerts. I carried out this mains fail test for both set and unset modes with the same result.

 

Do I have to enable logging for this type of event somehow, or should it be enabled automatically? Or perhaps there's a timer on mains fail events and I didn't leave the mains off long enough?

 

Any ideas?

 

thanks

John

Link to comment
Share on other sites

  • 4 weeks later...

OK, I've finally sussed this one out, stumbled upon the answer the other day.

 

A footnote on one of the back pages explains that AC fail events are only reported in the log if the condition persists for longer than 15-18 minutes (time chosen at random it says in the manual).

 

John

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use.