Nhoj Posted November 28, 2008 Posted November 28, 2008 Having just commissioned a 9651 I've been testing out event logging for the system. I isolated the mains supply, hopping to invoke a mains fail alert. The RKP recorded the event properly, but interrogation of the event log showed no mains fail alerts. I carried out this mains fail test for both set and unset modes with the same result. Do I have to enable logging for this type of event somehow, or should it be enabled automatically? Or perhaps there's a timer on mains fail events and I didn't leave the mains off long enough? Any ideas? thanks John Quote
Nhoj Posted December 22, 2008 Author Posted December 22, 2008 OK, I've finally sussed this one out, stumbled upon the answer the other day. A footnote on one of the back pages explains that AC fail events are only reported in the log if the condition persists for longer than 15-18 minutes (time chosen at random it says in the manual). John Quote