luboz Posted May 17, 2010 Share Posted May 17, 2010 I am trying to install Scantronic 9448EUR-90 board with two Takex MS100E multi pattern sensors connected in series on Zone 2 (all other zones are disabled) and Elmdene Quartz 1000live sounder. My problem is that control panel shows temper fault - all boxes are closed, all cable connections verified. If I reset the panel by disconnecting battery and main supply the temper light will go off Zone 2 light will go on and when you try to set the alarm with users code the temper lights come up on again. Could somebody recommend how I can solved the problem? Quote Link to comment Share on other sites More sharing options...
FastCar Posted May 17, 2010 Share Posted May 17, 2010 Your panel will not set with a tamper fault.You need to find out which tamper circuit is at fault , global tamper , bell tamper or case tamper.If you place a link across A/T then close the panel and reset , if the fault clears , then you have a fault on that circuit.Try the same on the bell tamper ( link between 0V and TR at the bell terminals). Quote Link to comment Share on other sites More sharing options...
luboz Posted May 18, 2010 Author Share Posted May 18, 2010 Thank you for your reply we found a problem with sounder circuit. Thanks again Quote Link to comment Share on other sites More sharing options...